208/120V panel AIC rating

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
See attached pix of existing 208/120V panel, does anyone know why all breakers on left side are 65KA
while the one on right side are 10KA? This is 208/120V panel, I imagine panel AIC rating is 10KA or less.
Did they paint the breakers on left side with wrong KA value? Strange!!!
 

Attachments

  • 01.JPG
    01.JPG
    424.4 KB · Views: 43
  • 02.JPG
    02.JPG
    653.4 KB · Views: 41

ron

Senior Member
There are way too many contractors that do not appreciate the importance and code requirements of short circuit ratings that should.

That is probably why there is a mismatch.
 

jap

Senior Member
Occupation
Electrician
Very doubtful the labels are wrong.
Very doubtful someone added that many different breakers to only one side.
It doesn't look like that panel has been added to.

My guess would be that it came from the factory that way where they filled with what they had to get it out the door.

JAP>
 

anbm

Senior Member
Location
TX
Occupation
Designer
Turn out the panel directory noted this panel is series rated @ 65KAIC, there are no other labels for series breaker rating or testing.:)
 

anbm

Senior Member
Location
TX
Occupation
Designer
So what's the issue?

JAP>
The issue is the panel and 10KA breakers have no labels that the breakers were tested for series rating, I guess? Thought this is required by NEC?
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
The issue is the panel and 10KA breakers have no labels that the breakers were tested for series rating, I guess? Thought this is required by NEC?
I thought the series rating information could be behind the equipment dead front and don't need to be readily visible
 
I thought the series rating information could be behind the equipment dead front and don't need to be readily visible
(C) Tested Series Combination Systems. Equipment encsures for circuit breakers or fuses applied in compliance with the series combination ratings marked on the equipment by the manufacturer in accordance with 240.86(B) shall be legibly marked in the field to indicate the equipment has been applied with a series combination rating. The marking shall meet the requirements in 110.21(B) and shall be readily visible and state the following: CAUTION — SERIES COMBINATION SYSTEM RATED ____ AMPERES. IDENTIFIED REPLACEMENT COMPONENTS REQUIRED
 

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
(C) Tested Series Combination Systems. Equipment encsures for circuit breakers or fuses applied in compliance with the series combination ratings marked on the equipment by the manufacturer in accordance with 240.86(B) shall be legibly marked in the field to indicate the equipment has been applied with a series combination rating. The marking shall meet the requirements in 110.21(B) and shall be readily visible and state the following: CAUTION — SERIES COMBINATION SYSTEM RATED ____ AMPERES. IDENTIFIED REPLACEMENT COMPONENTS REQUIRED
I see this a field installation requirement.
 
Status
Not open for further replies.
Top