Re: 208 and 240
The open Y primary, open delta secondary is still very much alive and well. We install them every day in this area. We call the larger transformer a
lighter or lighting transformer because it supplies the lighting loads as well as the 120 volt loads. The other transformer we call the
kicker because it kicks up the high phase.
We can have a small three phase load develop for a service station on a corner and just add a kicker to an existing transformer to give it a three phase service. The existing single phase loads will still be on the lighter.
Ed, we have had some businesses take services as you describe, a single phase and a three phase from the same bank.
To drive home what Tom has said, be sure you use full voltage rated circuit breakers on your three phase loads. Breakers with the slash rating are fine with the single phase 240 and 120 volt loads.
If the three phase load picks up, a third transformer will have to be added to support the delta.
It is interesting to note that another electric utility in Indiana uses an open delta configuration to serve lift stations where the load is straight 240 volt delta. They corner ground the common corner and connect the service with a triplex service drop. The customer sets a straight 240 volt single phase panelboard that is rated for a corner grounded, three phase service, uses full voltage rated two pole circuit breakers, and they are in business.
Except for having two transformers, it looks like a single phase service. You have a triplex drop, only two buses for the circuit breakers, and two pole breakers. You will read 240 volts between the phases and 240 volts to the grounded conductor (
not the neutral) from either phase.
I think I have rattled on too much.