I have been looking at a lighting job the last couple of days and have been having questions about how the over current protection is working.
The building has three separate bays in it. Each bay has 7, 400 watt metal halide fixtures in each bay. They have a FLA of 2.4 each. They operate at 208 volts single phase.
Here is the issue. All three bays of light fixtures are fed off of a three phase, 30 amp breaker. Each bay has a 3 pole lighting contactor controlling the light for the area. They bring all three legs into the contactor and then split the three phases up in each one of the bays. I am not sure how the load is distributed. The contactors are controlled with a 120 volt coil and they use a different phase of the three phase power for the control ckt to each bay.
If you do the math for the 30 amp 3 phase ckt, you have a VA of 10,800. 30 amps x 1.73 x 208. You surely can?t use this number for the load calc. My biggest question is how this can be code. I understand that the NEC is not a design manual, and was wondering if anybody has seen this before. Can you use a 3 pole breaker and evenly distribute the load for single phase 208? And, would you not have a total load for all 21 lights of 8400 VA? But wouldn?t you use the ballast rating of 2.4 amps apiece and come up with 50 amps?
Thanks for all the help
The building has three separate bays in it. Each bay has 7, 400 watt metal halide fixtures in each bay. They have a FLA of 2.4 each. They operate at 208 volts single phase.
Here is the issue. All three bays of light fixtures are fed off of a three phase, 30 amp breaker. Each bay has a 3 pole lighting contactor controlling the light for the area. They bring all three legs into the contactor and then split the three phases up in each one of the bays. I am not sure how the load is distributed. The contactors are controlled with a 120 volt coil and they use a different phase of the three phase power for the control ckt to each bay.
If you do the math for the 30 amp 3 phase ckt, you have a VA of 10,800. 30 amps x 1.73 x 208. You surely can?t use this number for the load calc. My biggest question is how this can be code. I understand that the NEC is not a design manual, and was wondering if anybody has seen this before. Can you use a 3 pole breaker and evenly distribute the load for single phase 208? And, would you not have a total load for all 21 lights of 8400 VA? But wouldn?t you use the ballast rating of 2.4 amps apiece and come up with 50 amps?
Thanks for all the help