I have a building with a 120/240V open delta service. Equipment that was delivered is a new 3? packaged rooftop AC unit, and a new 3? dough mixer, both of which have a nameplate rating of 208V, not your typical 200-230.
I recommended bucking xformers to the customer which would be an extra since the prints show 208/240, but "corporate" and their " equipment supplier" are telling me they are good to go on the 240 system. Doesn't seem right to me, so I asked for documented permission from the manufacturers, which I have yet to receive.
Is there an NEC violation if these are connected to a 240V 3? system other than possibly 110.3(B)?
Is it just bad practice or am I even correct in not wanting to connect these?
Thanks for any help you may afford me.
I recommended bucking xformers to the customer which would be an extra since the prints show 208/240, but "corporate" and their " equipment supplier" are telling me they are good to go on the 240 system. Doesn't seem right to me, so I asked for documented permission from the manufacturers, which I have yet to receive.