Nope. Leave out the "/2" and the "120v". It is a single 2-wire circuit.So if i had a load of 4356W on a 208/1 phase system would I do this?
4356/208/2 = 10.47A x 120V = 1256.5VA per phase?
Be forewarned that adding 208 1? line-to-line loads, connected to the other line on a 3? system, will change the calculation a bit...Thank you Larry! I thought I was off there on something. Have a great day.