208 THREE PHASE .120 volt loads . line a 4 amps. line b 3 amps .line c 6 amps. amps on neutral 2.6 amps. is this correct .
 

adamscb

Senior Member
Location
USA
Occupation
EE
Seems reasonable to me. The current flowing on the neutral is showing that there's some load imbalance, but nothing to get worried about.
 

jumper

Senior Member
ry%3D400
 

domnic

Senior Member
Occupation
Electrical Contractor
208 three pase

208 three pase

208 v . line a 10 amps. line b 10 amps. amps on neutral 5 amps. ?
 

domnic

Senior Member
Occupation
Electrical Contractor
208 three phase

208 three phase. line a 8 amps. line b 3 amps. neutral amps = ?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
208 v . line a 10 amps. line b 10 amps. amps on neutral 5 amps. ?
If you had three 10 amp loads, neutral current would obviously be 0 amps. For every amp you deduct from one phase, the neutral current would rise the same one amp. Deduct 10 amps, neutral current rises 10 amps
 