Assuming 3 phase grounded system delta / Wye
35,000 VA / 208 x 1.732 = 97.15 i
Primary if max OCPD protection 97.15 x 250% = 243 i or (i think you cannot go up to next standard size breaker normally but this is a step up transformer?)
PRIMARY
so 225 ampere standard size primary side breaker with 4/0 THHN good for 230i at 75 degrees celcius
SECONDARY
Secondary 35,000 VA / 480 x 1.743 = 42.09 i amperes
42.09 i x 125% = 52.62 i or 53 amperes
Secondary OCPD 60 ampere maximum next size up standard breaker (if allowed) and a #6 AWG THHN good for 55 amperes at 60 degrees celcius (depends on equipment termination rating)
I am installing power for a large printer that is not on site yet but the printer manufacturer has supplied a 35 kva 208 to 480 transformer.
I need some help sizing both the primary and secondary conductors and OCP.
Hello, Trickyflea
Here's your answer.
Assuming 3 phase 480 volts primary side
208/120 volts secondary side
35 kVA transformer
2023 NEC Section 450.3(B)
Transformers 1,000 Volts or Less.....refers to use T.450.3(B).
Primary side first:
Step 1: 35 kVA x 1,000 = 35,000 VA
Step 2: 35,000 VA / 480 x 1.732 = 831.36.....................35,000 VA / 831.36 = 42.10 amps primary side amps
Step 3: Select primary OCPD.........250 % x 42.10 = 105.25 amps
Step 4: No Foot Note here, cannot round up to next size
Step 5: Because there's no Foot Note that allows us to round up, go to T.240.6 (A)
Standard Ampere Ratings for Fuses and Inverse Time Circuit Breakers............
There we select a 100 amp OCPD which is under the 105 amp which was our product of multiplying by 250 %
Now the secondary side:
Step 1: 35 kVA x 1,000 = 35,000 VA
Step 2: 35,000 VA / 208 x 1.732 = 360.25.................35,000 VA / 360.25 = 97.15 amps secondary side
Step 3: Select secondary OCPD.................125% x 97.15 = 121.44 amps
Step 4: We have a Foot Note # 1 that allows for round up of 125% thus......121.44 amps x 125% = 121.44 amps
Step 5: 121.44 amps and using T.240.6(A) and a Foot Note #1 found in T.450.3 (B) we round up to a 125 amp OCPD
A 125 amp OCPD for the secondary side protection.
There's no guess work involved here, it's straight out of the Code book.
Comments accepted
Thanks for reading