mcpritt

Member
Are their any UL standards which deal with a 208 Volt high leg termination? According to the NEC, the high leg must marked and terminated on "B" Phase, what requires a manufacturer to do this if the UL passes their equipment?

Thanks,
Charlie
 

templdl

Senior Member
Location
Wisconsin
Re: 208 Volt High Leg

208v commonly a wye voltage as in 208y/120. But the term "high leg" refers to a 3ph4w delta, such as a 240/120 system.
If you sketch a delta with a flat side at the bottom and mark the 'A' phase at the lower left corner, 'B' at the top, and 'C' at the lower right and make it as a simple 240v delta.
Now mark a point half way between the 'A' and 'C' marking it as 'X0'and is considered a neutral and grounded. Remember that you have 240v 1ph between A-C and with the X0 you have 120v between A-X0 and 120v between C-X0. So, between A-C you have basically a 120/240 1ph3w as you would have in a common residential service entrance.
Remember that 'B'? Between the 'B' phase corner, often referred to as the wild or bastard leg, and the X0 you will have 208v. With the X0 grounded you will have 120v to ground from the A and C phases and 208v from the b to ground. However, even so, I have not found a logical need for 208v 1ph.
Panels that are supplied for this application are marked as 240/120 3ph4w and the 'B' phase is conductor is orange and is terminated on the center bus.
If you have a couple of extra minutes check page 8 of this link out. Although the diagram is turned and flipped from my description it does show you how a panel is connected.
http://www.enm.com/training/siemenscourses/pnl_2.pdf
 

Brinkmann

Member
Re: 208 Volt High Leg

Don't know of an UL requirement to do so but, as a practical matter, control panels we build include a warning label to make sure the "high leg" is on phase B.
 

thinfool

Senior Member
Location
Kentucky
Re: 208 Volt High Leg

Originally posted by mcpritt:
According to the NEC, the high leg must marked and terminated on "B" Phase, what requires a manufacturer to do this if the UL passes their equipment?
The control panels that I have installed at this voltage have had control transformers for the control voltage(s). This makes the need for identifying the high leg unnecessary. If you were actually using the neutral, labeling would be necessary to avoid legal issues...like smoking the 110volt controls because the installer didn't know where to put the 'high' leg.

I have assumed that you are describing control panels, not load centers, panelboards or service equipment . These are covered by the NEC and definitely need proper installation and identification.
 

mcpritt

Member
Re: 208 Volt High Leg

Thanks for the reply's. I have a good understanding of how the 208 Volt system works. My problem is on a Generator. The manufacturer puts the high leg on the "A" phase because they want to. They say that they do not have to follow the recommendations of the NEC, that is for the installer. This is apparently true, I know need to know if UL has any requirements for this. I want to FORCE them to change, but I need something to back me.

Thanks,
Charlie
 

thinfool

Senior Member
Location
Kentucky
Re: 208 Volt High Leg

Originally posted by mcpritt:
Thanks for the reply's. I have a good understanding of how the 208 Volt system works. My problem is on a Generator. >> I want to FORCE them to change, but I need something to back me.

Thanks,
Charlie
I wish you well. In our area, the POCO requires us to put the high leg on the right in a 3 phase meter socket. We then transition the high leg to the center at the main disconnect to satisfy the NEC.
The only way I know to 'force' much of anything is to shop around to other mfr's to see if you can find one that is more cooperative, ie, take your business elsewhere.
 

George Stolz

Moderator
Staff member
Location
Windsor, CO NEC: 2017
Occupation
Service Manager
Re: 208 Volt High Leg

Can you please state the nominal voltage of this generator?

Is it 120/240, or is it 120/208?

Originally posted by mcpritt:
I want to FORCE them to change, but I need something to back me.
Why? Do you forsee someone opening this generator up to add circuits? :confused:

The identification is to keep people from accidentally feeding line-to-neutral loads from the high leg. So do your job in the panel, and it won't be a problem.

The internals of listed equipment is not covered under the NEC anyway.
 