208 Volt Tap

Status
Not open for further replies.

mrschadegg

Member
Location
kansas
Occupation
Electrician
I have wash machine with 208 volt single phase going to it with no neutral. I need to tap with control transformer for a 120 volt chemical feed line. The 208 volt is on a 40amp breaker with wash machine at FLA of 29 amps. Is it possible to 10' tap off the source 208 volt and add a control xfmr for the 120 volt outlet. Im asking this because i dont want to break containment by adding another circuit from the panel.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Certainly possible, Follow Art 450 & Art 240 for overcurrent protection requirements.
 
Status
Not open for further replies.
Top