I have a 60 amp 3 phase 480 volt equipment. I have 3 phase 208 volt at the MDP.
Transformer sizing
208x60x1.73=49.82KVA
Purchase a 75 KVA transformer
Line side wire and OCP sizing
75KVA divided by 1.73x208=208 amp line side
4/0 THHW-2 copper wire size
OCP 208amp x 1.25=260 amp OCP/ 300 amp OCP?
Load size wire and OCP sizing
480x60x1.73=50amp load
#8 copper USE wire size
OCP 50amp x 1.25=63 amp OCP/ 70 amp OCP
USE is being used due to the equipment is in a shed away from the MDP. There will be trenching.
I stopped calculating the voltage drop at 250 MCM al = 3.4 voltage drop.
The manufactory warrantee requires no more then 10% VD. It was redundant to match 480 volt wire sizing with this knowledge in hand.
#6 al USE = 32.36 VD/ 6.74 VD percentage
#4 al USE = 20.36 VD/ 4.24 VD percentage
#4 al USE is a happy medium for me
TO SUM UP
WE have a 75 KVA trans former
We have 4/0 copper THHW-2 line side wire with 300 amp fuses
#8 al USE load wire traveling 500 feet with a 70 amp OCP
What's wrong with picture?
Transformer sizing
208x60x1.73=49.82KVA
Purchase a 75 KVA transformer
Line side wire and OCP sizing
75KVA divided by 1.73x208=208 amp line side
4/0 THHW-2 copper wire size
OCP 208amp x 1.25=260 amp OCP/ 300 amp OCP?
Load size wire and OCP sizing
480x60x1.73=50amp load
#8 copper USE wire size
OCP 50amp x 1.25=63 amp OCP/ 70 amp OCP
USE is being used due to the equipment is in a shed away from the MDP. There will be trenching.
I stopped calculating the voltage drop at 250 MCM al = 3.4 voltage drop.
The manufactory warrantee requires no more then 10% VD. It was redundant to match 480 volt wire sizing with this knowledge in hand.
#6 al USE = 32.36 VD/ 6.74 VD percentage
#4 al USE = 20.36 VD/ 4.24 VD percentage
#4 al USE is a happy medium for me
TO SUM UP
WE have a 75 KVA trans former
We have 4/0 copper THHW-2 line side wire with 300 amp fuses
#8 al USE load wire traveling 500 feet with a 70 amp OCP
What's wrong with picture?