I have some 208V/1P air conditioners that need factored into service sizes on a large multi-family development. The manufacturer's literature provides loads in MCA. Let's say an MCA is 11.6A.
The formula I know for converting into VA is: A*V*sqrt(PH)=VA. I've always assumed on a 208V/1P branch circuit that the phase is 1, so in this case the VA would be 11.6A*208V*sqrt(1)=2413VA. However I recently heard a respected engineer comment that this (or something similar to it) is a common mistake, and that the square root of three should be used. So VA would be 11.6A*208V*sqrt(3)=4174VA.
Obviously this makes a noticeable difference in load calcs when adding 200+ of these onto a pair of 208V/3P transformers. I've always calculated it using square root of 1, and never had anyone question me (or have services be overloaded) so I think sqrt(1) is correct. Anyone want to chime in? Is there an instance where sqrt(3) -should- be used in a single phase application?
Thanks!
The formula I know for converting into VA is: A*V*sqrt(PH)=VA. I've always assumed on a 208V/1P branch circuit that the phase is 1, so in this case the VA would be 11.6A*208V*sqrt(1)=2413VA. However I recently heard a respected engineer comment that this (or something similar to it) is a common mistake, and that the square root of three should be used. So VA would be 11.6A*208V*sqrt(3)=4174VA.
Obviously this makes a noticeable difference in load calcs when adding 200+ of these onto a pair of 208V/3P transformers. I've always calculated it using square root of 1, and never had anyone question me (or have services be overloaded) so I think sqrt(1) is correct. Anyone want to chime in? Is there an instance where sqrt(3) -should- be used in a single phase application?
Thanks!