steveve1
Member
- Location
- Tucson, AZ
Hi Guys! Well I'm sure this has been hashed out before, but I missed it. So here's the situation: On a service call to an existing industrial faculity with a 208 volt service. A standard 480v delta to 208Y/120 transformer is fed 208/3 to derive 480/3 for motor load (no neutral required). The transformer is 75kva, the primary over current protection (208v side) is 200a (LPN-RK), no secondary over current protection until the motor controller, 150' away, 100a circuit breaker then fusing. Secondary voltages (480v) seem fine when all is well. But in switching off the transformer for lock-out, then switching back on with no load, a primary fuse blew. Nothing to ground anywhere, all seems clear, installed new fuse, switch on - all good. Next day same thing. I'm thinking in-rush current is taking out the fuse (different phase each time). As the 208v side of things is connected wye, should X0 be grounded? It currently is not. I'm also thinking wrong transformer for the application, not to mention some over current concerns on the 480v secondary. Any thoughts? By the way, Happy Holiday Season to you and yours!