I'm feeding an existing 240V-3PH-3W panelboard via a transformer from a 208V service. I had specified a 208Y-240D transformer suitable for reverse connection, leaving X0 disconnected (per other posts on this forum). The contractor submitted a delta-delta transformer. Are there any issues with this if we don't ground the primary coils, just run the line wires and an equipment ground to the enclosure? secondary will be corner grounded delta. a diagram on the submittal sheet shows what appears to indicate H1 and X1 legs grounded. Electrically, I would think it would be okay, I just want to make sure I'm not overlooking something. Thanks,