InspectorPatches
Member
- Location
- University of Central Florida
- Occupation
- Electrical Inspector/plans reviewer 1
Hey everyone, I've got a question that I cant seem to find clarification in the code book regarding 3 phase receptacles being calculated at 180va. I have a panel calc submitted for plan review. They are calculating numerous 3ph 208v receptacles at 167va on each phase. Where they got that number I don't know. The area is for a lab and my gut tells me that the 3ph receptacles should be calculated by NEC 220.14(A), Specific loads and appliances, and not by NEC 220.14(I). To me I feel like there's info being intentionally left out so they can get approval to add this new equipment. Is there a NEC section that refers to 3 phase receptacle load or would it just be 180va if no info on specific appliances is provided?