208V on a 3 phase 240v high leg Delta?

Status
Not open for further replies.

wondervamp

Member
Location
SF Bay Area
Occupation
Shop technician
Howdy,

Can you get 208v 4 wire (3 phase/ground - no neutral) on a 240v high leg Delta system? I think you can only get 208V here with single phase on that high leg panel by going from the "high leg" and the neutral?

Thanks ya'll
 
You have it correct. A 240V high leg delta system has 208V to ground on the high leg, but no where else.

If you need 208V three phase, then you need a transformer. This could be some sort of buck/boost from your 240V supply (if you don't care about the 208V symmetry to ground) or it could be a 240:208V delta:wye transformer.

-Jon
 
Can you get 208v 4 wire (3 phase/ground - no neutral) on a 240v high leg Delta system?
Definitely not without a delta/wye or a B-B transformer.

I think you can only get 208V here with single phase on that high leg panel by going from the "high leg" and the neutral?
Yes, but you can't really use it that way.
 