208v on a single conductor

Toasted922

Member
Location
Boston
Occupation
Journeyman Electrician
Hey guys, so I have an odd issue. I have 208v single phase feeding a pole vac at a car wash. I was called out to get the vac up and running again. The feed comes through a 2” underground pvc conduit along with 5 other vac feeds and 1 lighting circuit shared between the 5 lights atop each vac. The first pull point after exiting the building is a handhole adjacent the pole vacs. In the handhole each leg reads normal for this circuit, 120v to ground with each leg and 208v between each leg, black and red. From there it dumps into a 3/4” pvc conduit exiting the handhole and goes directly to the inaccessible base of the pole vac and then up to a bell box for a service switch. After taking the switch apart to eliminate any kind of backfeed from the motor and/or the wiring the maintenance guys did, I tested at the pole vac to find 0 volts on the black and somehow 208 volts on the red conductor. The service to the building is 3 phase, 277/480v with a transformer inside giving us the 208 three phase. No bastard leg and the service is newly installed, hardly a year old. How is that possible to get 208v on a single conductor with no bastard leg and nothing else hooked up to the circuit to backfeed or interfere? The 3/4” pvc is filled to the brim with water as the maintenance fellas forgot to cap the vac pole, so theres ice given its been 20°F. My assessment was rip out the vac, pull new wires, put the vac back gingerly without damaging the conductors.
 
Last edited:

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Is this 120/208 three phase or 120/240 high leg delta? The high leg will have a bastard phase but the 120/208 will not. A 208 vacuum will have a 2 pole breaker if a 120/208 system
 

Toasted922

Member
Location
Boston
Occupation
Journeyman Electrician
Is this 120/208 three phase or 120/240 high leg delta? The high leg will have a bastard phase but the 120/208 will not. A 208 vacuum will have a 2 pole breaker if a 120/208 system
This is a typical 120/208v single phase circuit, no bastard leg. I checked the breaker first once I got the 208 on the single conductor. Everything checks out up to the handhole. After that I’m not sure how it’s happening. I verified its the correct wires using a circuit tracer first by opening and closing the breaker and voltage checked out. Then a toner when it was dead.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
What are you measuring each line against? I'm guessing the local conduit, which may actually be energized by the line you're reading zero volts against.

If I'm correct, it's lucky nobody has gotten shocked yet.

Why no breaker tripping? My first guess is poor bonding between the incoming and outgoing conduits in the hand-hole, if they're even metal, or a broken EGC.

Carefully check the voltage between the building's grounding system and the load-end's EGC with a long wire or an extension cord.
 

TwoBlocked

Senior Member
Location
Bradford County, PA
Occupation
Industrial Electrician
OP says correct voltage at handhole, but incorrect at vac, with vac not working, frozen water in conduit. I'd say the black leg broke in the conduit, but too much resistance in the water/ice to trip a breaker, and also too much resistance to run the vac, yet low enough resistance to energize the part of the black conductor going to where it can be read by the meter. A lower impedance meter (like the vac itself ;) ) would show little voltage between the legs.

Yep "...rip out the vac, pull new wires, put the vac back gingerly without damaging the conductors."
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
... I tested at the pole vac to find 0 volts on the black and somehow 208 volts on the red conductor. ...
I'm assuming you're measuring from each conductor to the metal bell box or something else you're assuming is ground. Always helps to be clear; voltage is always between two points. As discussed above, the explanation probably includes that the thing you're measuring to that you think is bonded or grounded is not.
 