jim dungar said:
Theoretically there is no reason that you would not be able to use the 208V L-N. The 208V L-N is as stable as the 240V L-L that completes the delta.
Practically there are many more reasons not to than there are to.
1) Most panels used with 240/120V 3P4W systems do not have 1-pole breakers rated for 208V to ground.
2) The transformers have not been sized to supply this amount of unbalanced load.
The real answer is very actual installation dependent. In fact it is possible to completely overload a poorly sized grounded delta transformer bank by connecting enough 120V L-N loads to only one phase.
That's what I was thinking
rattus said:
Let Vbn = 208V @ 90
Think of windings A-N and B-A in series. Z is 1.5X that of winding B-A
Ditto for windings C-N and B-C. Then,
Ztotal = 1.5/2 that of a full winding. But the real culprit is the PF.
Vbn = Van + Vba = Vcn + Vbc =
= 120 @ 0 + 240 @ 120 = 120 @ 180 + 240 @ 60 = 208V @ 90
For a resistive load, Ibn carries a phase angle of 90 degrees which is 90 degrees out of phase from Van and Vbn and 30 degrees out from Vba and Vbc.
(Unless I made a typo)
I
wasn't thinking that. . But now that I've read it a few times, it's sinking in ..... kinda.
"Ztotal = 1.5/2 that of a full winding."
So Z is low because of the two paths from highleg to neutral. . Are you saying this is a disadvantage or a problem ? . Is "weak source impedance" a bad thing ? . It sounds like a good thing to me.
"For a resistive load, Ibn carries a phase angle of 90 degrees which is 90 degrees out of phase from Van and Vbn and 30 degrees out from Vba and Vbc."
So does this mean alot of wasted power because of the 90? out of phase ?
rattus said:
OFF = 2400VA/2080VA = 1.154
You would have a similar situation if you loaded the wild leg.
So besides the usual losses, you take an additional "hit" because of the phase angle differences of 2 series phases that are out of phase with each other ? . Impedance in the source transformer, impedance in the load motor, resistance thruout the entire circuit
plus this additional loss ? .
In addition to the usual losses, you would still need 115.4va in the secondary to deliver 100w at the load ?
Am I seeing the issue here ?