I would greatly appreciate you all checking me on this:
My client has an infrared paint cure system for his spray booth. The system is 400V 3 phase 60Hz with FLA at 43.3. The machine manufacture says a 30KVA transformer will power their system. The voltage coming into the building is 208V Y 3 phase. Marcus transformer can build me a transformer 208V Y to 400V Y rated 83.3 primary fusing with secondary output at 43.4A. I realize the breaker or fusing on the primary side should be at least 125%, which would mean the breaker should be at least 104A. I am more inclined to go with a 125A fused disconnect. I can achieve this with a 125A rated sub feed lug coming from the 200A panel that will be less than 25ft from the disconnect and transformer location. (the 200A panel uses push in breakers, the sub feed lug will push in)
My biggest concern and question I have for you, is that the machine's load is essentially the same as the secondary output of the transformer. Should I be concerned about that if using a 30KVA transformer or should I step up to a 45KVA transformer. Again, the machine manufacturer says the 30KVA will do. If I go with the 45KVA transformer, then I will most likely have to change out the panel to a feed through panel so I can connect to a 150A primary side disconnect, which makes it a much bigger install.
Your thoughts are greatly appreciated!
My client has an infrared paint cure system for his spray booth. The system is 400V 3 phase 60Hz with FLA at 43.3. The machine manufacture says a 30KVA transformer will power their system. The voltage coming into the building is 208V Y 3 phase. Marcus transformer can build me a transformer 208V Y to 400V Y rated 83.3 primary fusing with secondary output at 43.4A. I realize the breaker or fusing on the primary side should be at least 125%, which would mean the breaker should be at least 104A. I am more inclined to go with a 125A fused disconnect. I can achieve this with a 125A rated sub feed lug coming from the 200A panel that will be less than 25ft from the disconnect and transformer location. (the 200A panel uses push in breakers, the sub feed lug will push in)
My biggest concern and question I have for you, is that the machine's load is essentially the same as the secondary output of the transformer. Should I be concerned about that if using a 30KVA transformer or should I step up to a 45KVA transformer. Again, the machine manufacturer says the 30KVA will do. If I go with the 45KVA transformer, then I will most likely have to change out the panel to a feed through panel so I can connect to a 150A primary side disconnect, which makes it a much bigger install.
Your thoughts are greatly appreciated!