Let's say the panel schedule load in VA is as follows: Location Commercial Strip Mall
PH-A Total Load = 19,276VA
PH-B Total Load = 19,085VA
PH-C Total Load = 17,781VA
PH-A: 19,276VA/208 = 92.673 = 93 Amperes
PH-B: 19,085VA/208 = 91.754 = 92 Amperes
PH-C: 17,781VA/208 = 85.486 = 85 Amperes
Next Panel Size Up = 100 Ampere Panel
Assume that any (LCL) Continuous Loads have been factored into the example.
Why are loads calculated by dividing the load by 208V when OCPD sizing is calculated by dividing the branch circuit load by 120V?
Correct me if I have made any mistakes, I have lots to learn.
Thanks,
--Mario