Hello,
I am an MEP electrical designer. For years I have always thought that if you have a 208V single phase load fed from a 208Y/120V panel, meaning there is a 2 pole breaker, and you want to know the per phase kVA to input into a panel schedule, you simply take the voltage (208v) and multiply by the FLA/MCA which in my case is 25 amps, then divide by 2 to get the kVA per pole for the panel schedule.
It would look like this:
208V * 25A = 5200VA = 5.2kVA
5.2kVA / 2 = 2.6kVA
So the first pole on the schedule would have 2.6kVA and the second pole would also have 2.6kVA.
I am receiving feedback on my schedule that the load per phase should acutally be calculated as:
5.2kVA/sqrt3 = 5.2kVA/1.73 = 3.002kVA, and the first pole on the schedule would have 3.002kVA and the second pole would also have3.002kVA.
Let me know what you guys think, Thanks!
I am an MEP electrical designer. For years I have always thought that if you have a 208V single phase load fed from a 208Y/120V panel, meaning there is a 2 pole breaker, and you want to know the per phase kVA to input into a panel schedule, you simply take the voltage (208v) and multiply by the FLA/MCA which in my case is 25 amps, then divide by 2 to get the kVA per pole for the panel schedule.
It would look like this:
208V * 25A = 5200VA = 5.2kVA
5.2kVA / 2 = 2.6kVA
So the first pole on the schedule would have 2.6kVA and the second pole would also have 2.6kVA.
I am receiving feedback on my schedule that the load per phase should acutally be calculated as:
5.2kVA/sqrt3 = 5.2kVA/1.73 = 3.002kVA, and the first pole on the schedule would have 3.002kVA and the second pole would also have3.002kVA.
Let me know what you guys think, Thanks!