cottora
Senior Member
- Location
- Atlanta, GA
The more I read on this the more I tie my brain in knots...Without considering derating of equipment for continuous load, if I have balanced L-L (208v) loads on a 1000kVa transformer, I get 1000 x 1000/(1.73 x 208) = ~2775-Amp rating for such transformer.
Does this mean that the maximum number of 208v L-L 6-Amp loads the transformer can handle is 462 (2775/6 = 462)?
This doesn't seem to add up because a 6-Amp 208v single-phase load is 1.248kVa (so we get 1000/1.248 = 801 allowable 6-Amp 208v loads)
I think my mistake is either 1) not using the neutral "derates" the transformer or 2) I must multiply the first calculation by 1.73 to account for phasing between the lines
Thanks in advance!
Does this mean that the maximum number of 208v L-L 6-Amp loads the transformer can handle is 462 (2775/6 = 462)?
This doesn't seem to add up because a 6-Amp 208v single-phase load is 1.248kVa (so we get 1000/1.248 = 801 allowable 6-Amp 208v loads)
I think my mistake is either 1) not using the neutral "derates" the transformer or 2) I must multiply the first calculation by 1.73 to account for phasing between the lines
Thanks in advance!