20A circuit.

Status
Not open for further replies.

jes25

Senior Member
Location
Midwest
I have been told you must use 20A branchcircuits in commercial applications. I can not find this in the code. I am running a dedicated circuit to a 7 amp freezer.
 

iwire

Moderator
Staff member
Location
Massachusetts
Re: 20A circuit.

That is not an NEC rule.

I have heard that some areas have rules like that.

There can also be job specifications that require 12 AWG min.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: 20A circuit.

I am running a dedicated circuit to a 7 amp freezer.
According to the NEC this would not require a 20 amp circuit or even require a dedicated circuit.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
Re: 20A circuit.

Most specifications for commercial or industrial areas seem to require all 20A outlets. IMO, it is a good idea in any case. The extra cost is minimal and with todays power hungry equipment, you cannot have enough outlets.
 