What is the NEC code section that says you can't put a
#14 jumper to a 15A device on a 20A ct.
If the 15A device is allowed by exception on the 20A ct then so is the 15A pigtail. Not mixing wire sizes here downstream, just to the 15A device.
Some 1990's installs I see all home runs in #12, cbs at 15A and then the lighting loops mixed down to #14, solid and better for voltage drop but no wire sizes/color changes allowed. The next guy might get confused. Forget about ring circuits at 120v, pressurized gas pipe hangers or the color scheme in Bahrain!
:grin:
#14 jumper to a 15A device on a 20A ct.
If the 15A device is allowed by exception on the 20A ct then so is the 15A pigtail. Not mixing wire sizes here downstream, just to the 15A device.
Some 1990's installs I see all home runs in #12, cbs at 15A and then the lighting loops mixed down to #14, solid and better for voltage drop but no wire sizes/color changes allowed. The next guy might get confused. Forget about ring circuits at 120v, pressurized gas pipe hangers or the color scheme in Bahrain!
:grin: