Engineer shows a 208V 30A multi outlet assembly in IT rack fed from 20A breaker. Can't have that correct?
I agree with you not permitted. If you have a 20 amp OCPD you can 20 amp conductors but for a multi-outlets you cannot use 30 amp devices.Engineer shows a 208V 30A multi outlet assembly in IT rack fed from 20A breaker. Can't have that correct?
210.23 Permissible Loads, Multiple-Outlet Branch Circuits. In no case shall the load exceed the branch-circuit ampere
rating. A branch circuit supplying two or more outlets or receptacles shall supply only the loads specified according to its size
as specified in 210.23(A) through (D) and as summarized in 210.24 and Table 210.24.
I'm a little lost..surprise..lol. The rack equip plugs into the MOA.I agree with you not permitted. If you have a 20 amp OCPD you can 20 amp conductors but for a multi-outlets you cannot use 30 amp devices.
Table 210.21(B)(3) Receptacle Ratings for Various Size Circuits lists 20 amp: either 15 or 20 amp receptacles. A single 30 amp receptacle on a 20 amp circuit would be permitted.
Is this outlet strip hard-wired or plugged it?
Can you provide more detail, especially how the MOA is connected to the power source? Is it cord and plug connected to a 30 amp single receptacle outlet fed by a 208 volt, 20 amp breaker?