20A Feedthrough on 15A Receptacle

Status
Not open for further replies.

ChrisFV

Member
Location
NC
Occupation
Electrician Student
The Code permits 15A receptacles on a multi-outlet 20A branch circuit. This implies that the 15A receptacle must support 20A feedthrough, in order to feed a possible 20A load downstream. But is this 20A feedthrough capability actually spec'd anywhere, either in the Code or in UL listing for the receptacle?
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
A receptacle is not a feedthrough actually. In fact, a preferred method for wiring a receptacle that is not at the end of the run is to pigtail the hot and neutral and connect the pigtail to the receptacle. If you have a backwired device, you might put both wires under either end of the backwire plate, but that's not feedthrough either.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
The Code permits 15A receptacles on a multi-outlet 20A branch circuit. This implies that the 15A receptacle must support 20A feedthrough, in order to feed a possible 20A load downstream. But is this 20A feedthrough capability actually spec'd anywhere, either in the Code or in UL listing for the receptacle?
The binding screw parts of the 15 amp receptacle are actually rated for 20 amps as part of the listing of the device. The feed-through current isn't actually going through the entire device it's just passing from one binding screw to another.
 
A receptacle is not a feedthrough actually. In fact, a preferred method for wiring a receptacle that is not at the end of the run is to pigtail the hot and neutral and connect the pigtail to the receptacle. If you have a backwired device, you might put both wires under either end of the backwire plate, but that's not feedthrough either.
How is it not a feed-through? Granted there is no definition of "feed through" anywhere but in practice I think most of us would call it feeding through.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
How is it not a feed-through? Granted there is no definition of "feed through" anywhere but in practice I think most of us would call it feeding through.
I agree, feed-through is a common term used when there is no pigtailing.
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
From the UL Guide Information for Receptacles (RTRT)
Single and duplex receptacles rated 15 and 20 A that are provided with more than one set of terminals for the connection of line and neutral conductors have been investigated to feed branch-circuit conductors connected to other outlets on a multi-outlet branch circuit, as follows:
  • Back-wire (screw-actuated clamp type) terminations with multiple wire-access holes used concurrently to terminate more than one conductor
  • Side-wire (binding screw) terminals used concurrently with their respective push-in (screwless) terminations to terminate more than one conductor
 

tthh

Senior Member
Location
Denver
Occupation
Retired Engineer
Ok, I get the usage of the term there - even if I don't think it is properly descriptive. The binding post or backwire plate is just another wire nut more or less.

When I think of feed through, I think more like GFCI receptacles.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
The receptacle rating describes the slot configuration, not the conductive parts' ampacity. Most 15a and 20a receptacles of a given grade contain the same internal parts.

In the pic, note that, in the receptacle on the right, the Triple-wipe Contacts in the red box, either a horizontal or vertical blade will fit, and be touched in three places by the internal conductive parts. All they have to do to make a 20a version and/or a 250v receptacle, is put on a different face, either vertical, horizontal or T-shaped for each slot: