I have a 20KW, 240V single phase furnace. The blower fan draws 7.6 amps. The furnace has two 60 amp breakers on it to land the two branch circuits that feed the unit.
The name plate states that the circuit that includes the blower fan minimum circuit ampacity is 61.59 amps. (10KW/240 + 7.6 for fan x 1.25 for continuous load) The other circuit’s listed minimum ampacity is 52 amps. However, the fields wiring requirements for the install require a 60 amp breaker for both branch circuits and NEC 424.22 requires heaters to have 60 amp overcurrent max. But NEC 210.20 requires overcurrent for continuous load to be no less than 125% of full load current. I am a bit confused. It is only 1.5 amps but still… Is this a legal install?
PART II
This furnace is for a dwelling unit. The name plate says use #6 wire with at least a 75 degree rating. The wire in MN is THHN and has a 90 degree rating. I know NM ampacity is from the 60 degree table. It is my contention that, despite what the name plate says, a 6/2 NM branch circuit may feed the 52 amps furnace load, but a 4/2 NM or a raceway with 75 degree rated #6 conductor must feed the 61.59 amp furnace load. Is this correct?
The name plate states that the circuit that includes the blower fan minimum circuit ampacity is 61.59 amps. (10KW/240 + 7.6 for fan x 1.25 for continuous load) The other circuit’s listed minimum ampacity is 52 amps. However, the fields wiring requirements for the install require a 60 amp breaker for both branch circuits and NEC 424.22 requires heaters to have 60 amp overcurrent max. But NEC 210.20 requires overcurrent for continuous load to be no less than 125% of full load current. I am a bit confused. It is only 1.5 amps but still… Is this a legal install?
PART II
This furnace is for a dwelling unit. The name plate says use #6 wire with at least a 75 degree rating. The wire in MN is THHN and has a 90 degree rating. I know NM ampacity is from the 60 degree table. It is my contention that, despite what the name plate says, a 6/2 NM branch circuit may feed the 52 amps furnace load, but a 4/2 NM or a raceway with 75 degree rated #6 conductor must feed the 61.59 amp furnace load. Is this correct?