- Tennessee NEC:2017
- Occupation
- Semi-Retired Electrician
I just a had a rough-in inspection and the inspector is asking for an additional branch circuit be run to the laundry. I have five receptacles on the one circuit that I ran. One receptacle is behind the washer, one is for a gas water heater (which pulls next to nothing) and the other three are just convenience receptacles along the wall.
I'm not seeing in 210.11(C)(2) where it requires me to have only one receptacle, or any number of receptacles, on the circuit. It just says there shall be no other outlets, which to me means not leaving the laundry room to serve other outlets or the lights in the laundry.
Am I mis-reading it?
I'm not seeing in 210.11(C)(2) where it requires me to have only one receptacle, or any number of receptacles, on the circuit. It just says there shall be no other outlets, which to me means not leaving the laundry room to serve other outlets or the lights in the laundry.
Am I mis-reading it?
(2) Laundry Branch Circuits. In addition to the number of
branch circuits required by other parts of this section, at least
one additional 20-ampere branch circuit shall be provided to
supply the laundry receptacle outlet(s) required by 210.52(F).
This circuit shall have no other outlets.