210.11(C)(3) Exception
[Revise text]
Existing text
Bold = add text
[Substantiation]
(1)The exception to 210.23(A) disallows outlets other than "receptacle outlets specified" while the exception to 210.11(A) is specifically permitting outlets other than receptacle outlets.
(2) There are no restrictions or allowances in 210.23(A) that change the application of 210.11(C)(3). The reference to 210.23(A) is unnecessary.
_________________________________________________________________________________
I don't have 2005 so this text might not be current. My understanding is that this imperfection still exists in 2005.
Basically, 210.23(A) (outside of the exception) says you can put anything you want on the circuit. There's hardly a need to make sure we read that.
It looks like they were having trouble seperating what should be in "Branch Circuits" and what should be in "Permissable Loads" and somebody came up with the inovative idea of looping them together.
[Revise text]
Existing text
Proposed textWhere the twenty-ampere circuit supplies a single bathroom, outlets within the same bathroom shall be permitted to be supplied in accordance with 210.23(A)
Italics = strike textWhere the twenty-ampere circuit supplies a single bathroom, that circuit shall be permitted to supply other outlets within the same bathroom.
Bold = add text
[Substantiation]
(1)The exception to 210.23(A) disallows outlets other than "receptacle outlets specified" while the exception to 210.11(A) is specifically permitting outlets other than receptacle outlets.
(2) There are no restrictions or allowances in 210.23(A) that change the application of 210.11(C)(3). The reference to 210.23(A) is unnecessary.
_________________________________________________________________________________
I don't have 2005 so this text might not be current. My understanding is that this imperfection still exists in 2005.
Basically, 210.23(A) (outside of the exception) says you can put anything you want on the circuit. There's hardly a need to make sure we read that.
It looks like they were having trouble seperating what should be in "Branch Circuits" and what should be in "Permissable Loads" and somebody came up with the inovative idea of looping them together.