So here is my situation i had and inspection today.
master bathroom has 2 dedicated circuits ran to it
Circuit A lands in a box for a single gfci in between two sinks this circuit serves nothing else and stops there. Satisfying 210.11 c3 in my opinion
Circuit B lands in a 3 Gang box 2 switches for bathroom lights and one gfci (customer wanted another one) this box his also on the edge of the sink on top of the vanity but this gfci would not satisfy the code as it is to far from the second sink. this circuit also jumps to an adjacent closet to feed the lights.
Inspector is sighting 210.11 c3 stating the bathroom receptacles Shal not feed any other outlets. i would agree with him if circuit b was the only circuit there
My question and thinking is as long as i have one (circuit A) satisfying 210.11 C3 im good. the way i read it is that it says AT LEAST ONE not all.?
what say you guys?
master bathroom has 2 dedicated circuits ran to it
Circuit A lands in a box for a single gfci in between two sinks this circuit serves nothing else and stops there. Satisfying 210.11 c3 in my opinion
Circuit B lands in a 3 Gang box 2 switches for bathroom lights and one gfci (customer wanted another one) this box his also on the edge of the sink on top of the vanity but this gfci would not satisfy the code as it is to far from the second sink. this circuit also jumps to an adjacent closet to feed the lights.