Exhibit 210.11 in the hand book says three receptacles required to have GFCI protection and one that is not. But if you reed the print on the picture all 4 are required to have GFCI protection. Is this a missprint?
 

bphgravity

Senior Member
Location
Florida
The exhibit is pointing to three receptacles requiring GFCI protection, and one receptacle that is required to be GFPE protected. Read the full comment associated with the exhibit...
 