Section/Paragraph: 210.12(A)(6) AFCI. Dwelling Units.
Deleted Text
(6) Where a listed metal or nonmetallic conduit or tubing or Type MC cable is encased in not less than 50 mm (2 in.) of concrete for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a listed outlet branch-circuit type AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.
Substantiation:
"metal or nonmetallic" means ANY, it adds no restriction or information to this section. The operative part of this section is "encased in concrete".
Inserted Deleted
Deleted Text
(6) Where a listed metal or nonmetallic conduit or tubing or Type MC cable is encased in not less than 50 mm (2 in.) of concrete for the portion of the branch circuit between the branch-circuit overcurrent device and the first outlet, it shall be permitted to install a listed outlet branch-circuit type AFCI at the first outlet to provide protection for the remaining portion of the branch circuit.
Substantiation:
"metal or nonmetallic" means ANY, it adds no restriction or information to this section. The operative part of this section is "encased in concrete".