Steve Sink
Member
- Location
- NC
1. 210.12(B) Dwelling Unit Bedrooms. All 120-volt single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
Branch/feeder AFCIs shall be permitted to be used to meet the requirements of 210.12(B) until January 1, 2008.
2. Proposal recommends: deleted text
3. Proposal: (Words to be deleted in parentheses)
All 120-volt single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
Branch/feeder AFCIs shall be permitted to be used to meet the
requirements of 210.12(B) until January 1, 2008.
4. Substantiation: It seems as if there would be a way around putting arc-fault
protection in dwelling unit bedrooms if the branch circuits covered by the Code
only listed 15- and 20-ampere branch circuits. One could get around installing
arc-fault protection simply by installing either a 10- or 30-ampere breaker. If a
30-ampere breaker was installed on the circuit using #14 AWG then the insulation
could break down during a fault and cause a fire. Table 310.16 says that #14
AWG is only good for 20-amperes.
Branch/feeder AFCIs shall be permitted to be used to meet the requirements of 210.12(B) until January 1, 2008.
2. Proposal recommends: deleted text
3. Proposal: (Words to be deleted in parentheses)
All 120-volt single phase, 15- and 20-ampere branch circuits supplying outlets installed in dwelling unit bedrooms shall be protected by a listed arc-fault circuit interrupter, combination type installed to provide protection of the branch circuit.
Branch/feeder AFCIs shall be permitted to be used to meet the
requirements of 210.12(B) until January 1, 2008.
4. Substantiation: It seems as if there would be a way around putting arc-fault
protection in dwelling unit bedrooms if the branch circuits covered by the Code
only listed 15- and 20-ampere branch circuits. One could get around installing
arc-fault protection simply by installing either a 10- or 30-ampere breaker. If a
30-ampere breaker was installed on the circuit using #14 AWG then the insulation
could break down during a fault and cause a fire. Table 310.16 says that #14
AWG is only good for 20-amperes.