Can someone please explain (in detail) the "before the application of any adjustment or correction factors" when determining the allowable ampacity of branch circuit and feeder conductors. Thank you.
You may or may not have to derate the conductor's ampacity based on the number of current carrying conductors in a raceway and also based on the ambient temperature at which the conductors will be operating.
Let me re-phase that...let's take a scenario with a branch circuit conductor that has continuous and non-continuous loads in a conduit with six additional current carrying conductors in an ambient tempature of 100-degrees F. In this case "adjustment or correction factors" are required. Do you apply these adjustments or correction factors before or after you calculate 125% of the continuous and 100% of the non-continuous?