Can someone please explain (in detail) the "before the application of any adjustment or correction factors" when determining the allowable ampacity of branch circuit and feeder conductors. Thank you.
 
You may or may not have to derate the conductor's ampacity based on the number of current carrying conductors in a raceway and also based on the ambient temperature at which the conductors will be operating.

These are the adjustment and correction factors.
 
Let me re-phase that...let's take a scenario with a branch circuit conductor that has continuous and non-continuous loads in a conduit with six additional current carrying conductors in an ambient tempature of 100-degrees F. In this case "adjustment or correction factors" are required. Do you apply these adjustments or correction factors before or after you calculate 125% of the continuous and 100% of the non-continuous?
 
After. You calculate the conductor size, then apply the correction factors.

And, yes, you do have to "double derate". Number of conductors and ambient. In either order - makes no difference.
 
You are discussing two different things. You do one, then you do the other, as Brad said.

First, you determine the load. That's when the 125% and 100% come into play. That tells you what ampacity the conductors are going to have to have.

Then you pick a conductor, and see if it has the necessary ampacity. In determining the conductor's ampacity, you have to apply the derating factors.
 