210.19(A)(1) General. Branch-circuit conductors shall have an ampacity not less than the larger of 210.19(A)(1)(a) or (A)(1)(b) and comply with 110.14(C) for equipment terminations. (a)Where a branch circuit supplies continuous loads or any combination of continuous and noncontinuous loads, the minimum branch-circuit conductor size shall have an ampacity not less than the noncontinuous load plus 125 percent of the continuous load in accordance with 310.14. (b)The minimum branch-circuit conductor size shall have an ampacity not less than the maximum load to be served after the application of any adjustment or correction factors in accordance with 310.15.
Exception No. 1 to (1)(a): If the assembly, including the overcurrent devices protecting the branch circuit(s), is listed for operation at 100 percent of its rating, the ampacity of the branch-circuit conductors shall be permitted to be not less than the sum of the continuous load plus the noncontinuous load in accordance with 110.14(C).
Exception No. 2 to (1)(a) and (1)(b): Where a portion of a branch circuit is connected at both its supply and load ends to separately installed pressure connections as covered in 110.14(C)(2), it shall be permitted to have an allowable ampacity, in accordance with 310.15, not less than the sum of the continuous load plus the noncontinuous load. No portion of a branch circuit installed under this exception shall extend into an enclosure containing either the branch-circuit supply or the branch-circuit load terminations.