TM1238
Member
- Location
- Buffalo, NY
A co-worker and myself have a difference of opinion on conductor sizing for a large RTU. The unit in question has a MOCP of 400A and an MCA of 366A. The unit is served by a 400A breaker and it will be fed with a set of parallel aluminum conductions. My assertion is that a parallel set of 250 MCM AL must be utilized to satisfy 210.19 (the conductor current carrying capacity must meet or exceed the rating of the load) 410A exceeds the MCA of 366A. My co-worker argues that 4/0 AL can be utilized because 240.4B allows "rounding up" to the next sized overcurrent protection. While I agree 240.4B allows this, I disagree that parallel 4/0 AL are code compliant since a parallel set is only rated to carry 360A, below the MCA of 366A. So 250's or 4/0's?