I'm embarrassed to ask but I am going to anyway just to confirm either way as I am always subject to error. Lol
I have a 11kw electric range @240v. 8kw/240=33.3 next size up is 40amperes OCPD. The only available cord for this range that the sales rep of 15 years gives me is a 50A rated cord 3 or 4 wire and I'm using a 4 wire of course. Yes this is H-Depot. My question is.... Can we install a 8/3 NMC on a 50A rated receptacle if it is protected at 40 amperes? The problem I have with this is if the home owner changes this range out with a induction style range rated to be protected at 50amperes and the breaker trips guess what? The home owner changes out the breaker from a 40A to a 50A because the receptacle is a 50 A so we're good! Well now we have a #8awg fuse because @ the 60 degree column this wire is only good for 40 Amperes. The 15 year sales rep says that this is what they do in Arizona were he originally lived prior to coming to Alaska. I wanted to say we can only get away with that here but definitely not Arizona. :lol:
I have a 11kw electric range @240v. 8kw/240=33.3 next size up is 40amperes OCPD. The only available cord for this range that the sales rep of 15 years gives me is a 50A rated cord 3 or 4 wire and I'm using a 4 wire of course. Yes this is H-Depot. My question is.... Can we install a 8/3 NMC on a 50A rated receptacle if it is protected at 40 amperes? The problem I have with this is if the home owner changes this range out with a induction style range rated to be protected at 50amperes and the breaker trips guess what? The home owner changes out the breaker from a 40A to a 50A because the receptacle is a 50 A so we're good! Well now we have a #8awg fuse because @ the 60 degree column this wire is only good for 40 Amperes. The 15 year sales rep says that this is what they do in Arizona were he originally lived prior to coming to Alaska. I wanted to say we can only get away with that here but definitely not Arizona. :lol: