I was teach a couple of folks "Code" and came across a situation to which I could not find the answer.
Assume for a moment we have a dishwasher rated at 1200 w and a 1/2 HP garbage disposal.
By Code, could we put them on (1) 20 amp circuit
(For discussion ignore any manufacturer recommendations or advisability of doing so... limit the answer to Code compliance)
For me its a but grey.. the dishwasher is 1200w so it does not exceed the 50% load limit imposed by 210.23(A)(2) and a 1/2 hr motor is 9.8 amps per 430.28 so, by Table, it does not exceed the 50% rule (ignoring the 125% branch circuit rating)