Discussion here in the office in regards to 210.4 (B)
I believe that ALL multiwire branch circuits shall simultaneously disconnect REGARDLESS if a shared neutral (grounded conductor) or dedicated neutrals are in the cable.
Some here believe that if there are dedicated neutrals per each circuit, that single pole breakers are fine instead of simultaneous disconnecting of both circuits.
I believe that ALL multiwire branch circuits shall simultaneously disconnect REGARDLESS if a shared neutral (grounded conductor) or dedicated neutrals are in the cable.
Some here believe that if there are dedicated neutrals per each circuit, that single pole breakers are fine instead of simultaneous disconnecting of both circuits.