M mikey41949 New member Location Copperas Cove, TX Dec 16, 2009 #1 Is there any exception to section 210.4 B that will allow the use of single pole breakers instead of 2/3 pole breaker? Michael Tallon
Is there any exception to section 210.4 B that will allow the use of single pole breakers instead of 2/3 pole breaker? Michael Tallon
H Hendrix Senior Member Location New England Dec 16, 2009 #2 mikey41949 said: Is there any exception to section 210.4 B that will allow the use of single pole breakers instead of 2/3 pole breaker? Michael Tallon Click to expand... no, there aren't
mikey41949 said: Is there any exception to section 210.4 B that will allow the use of single pole breakers instead of 2/3 pole breaker? Michael Tallon Click to expand... no, there aren't
raider1 Senior Member Staff member Location Logan, Utah Dec 16, 2009 #3 Welcome to the forum. 210.4(B) does not necessarily require a 2 or 3 pole breaker. You can use single pole breakers with an identified handle tie to comply with this section. 210.4(B) does not require a common trip, just simultaneous disconnection. Chris