S Samuel87 Member Location Fresno CA Occupation Electrician Dec 20, 2021 #1 The article 210.4 is about multiwire branch circuit and I will think that the dryer or Is the dryer a multiwire branch circuit? thanks.
The article 210.4 is about multiwire branch circuit and I will think that the dryer or Is the dryer a multiwire branch circuit? thanks.
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician Dec 20, 2021 #2 Samuel87 said: The article 210.4 is about multiwire branch circuit and I will think that the dryer or Is the dryer a multiwire branch circuit? thanks. Click to expand... Read the definition of branch circuit, multiwire. Then see if the dryer, or the way its wired, meets that definition.
Samuel87 said: The article 210.4 is about multiwire branch circuit and I will think that the dryer or Is the dryer a multiwire branch circuit? thanks. Click to expand... Read the definition of branch circuit, multiwire. Then see if the dryer, or the way its wired, meets that definition.
D donghan82 Member Location New Jersey Occupation Electrical Engineer Dec 23, 2021 #3 Yes, the branch circuit serving the dryer is classified as a multiwire branch circuit per Article 210.4(C) Exception No. 1.
Yes, the branch circuit serving the dryer is classified as a multiwire branch circuit per Article 210.4(C) Exception No. 1.