Fred B
Senior Member
- Location
- Upstate, NY
- Occupation
- Electrician
House 1 is original house and has the pressure switch but distance is over 300ft to well and well 475ft deep so wishes to power the pump from the new house 2 under construction that is only 75ft to well. This is a concern to the customer so wishes to do the following. House 2 will now have a 400A meter disconnect to power both bldg. moved from a pedestal in mid yard.
Customer proposes this installation in drawing. House 1 to keep 120V power to pressure switch from house 1 source panel. Power to well pump receive power from house 2 panel through a contactor to be located at house 2. Conduit exists between all structures as he plans to run the 120V contactor control from house 1 to house 2.
I see this as an issue with 210.4(A) All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment. and (B)
Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates. As well as an issue with 430.75(A)
Customer proposes this installation in drawing. House 1 to keep 120V power to pressure switch from house 1 source panel. Power to well pump receive power from house 2 panel through a contactor to be located at house 2. Conduit exists between all structures as he plans to run the 120V contactor control from house 1 to house 2.
I see this as an issue with 210.4(A) All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment. and (B)
Each multiwire branch circuit shall be provided with a means that will simultaneously disconnect all ungrounded conductors at the point where the branch circuit originates. As well as an issue with 430.75(A)