hurk27
Senior Member
- Location
- Portage, Indiana NEC: 2008
I have an inspector who takes the second sentence of this code to say that it is requiring any SA circuit that feeds "kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit" has to also be the circuit that feeds one of the two or more counter SA circuits.
The problem is he is interpreting " the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all receptacle outlets covered" as requiring these SA circuits to have to serve both the counter and the other areas?
I tried to show him that this requirement is only to not allow these rooms on other than SA branch circuits, but he insists that it requires the counter circuit to serve these other outlets.
I have for years kept my counter circuits separate from any SA circuit feeding a dinning room or the like. I have never had this type of spin put on this requirement.
When we look at 210.52(B)(3) it permits you to supply receptacle outlets in the kitchen and other rooms with additional SA circuits.
Has anyone ever run into this?
The problem is he is interpreting " the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all receptacle outlets covered" as requiring these SA circuits to have to serve both the counter and the other areas?
I tried to show him that this requirement is only to not allow these rooms on other than SA branch circuits, but he insists that it requires the counter circuit to serve these other outlets.
I have for years kept my counter circuits separate from any SA circuit feeding a dinning room or the like. I have never had this type of spin put on this requirement.
When we look at 210.52(B)(3) it permits you to supply receptacle outlets in the kitchen and other rooms with additional SA circuits.
Has anyone ever run into this?