Note to self: Do not submit this proposal.
(What brought this on)
View non-bolded as struck through.
1.) NEC Section/Paragraph: 210.52(B)(3)
2.) Proposal Recommends: [deleted text]
3.) Proposal:
[ May 22, 2005, 11:02 AM: Message edited by: georgestolz ]
(What brought this on)
View non-bolded as struck through.
1.) NEC Section/Paragraph: 210.52(B)(3)
2.) Proposal Recommends: [deleted text]
3.) Proposal:
4.) Substantiation: The references to "two or more" SA's is redundant, already mentioned in 210.11(C)(1), and 210.52(B)(1). The "same kitchen" text could be more forcefully added to 210.52(B)(1), or dropped entirely.NEC-2005 210.52(B)(3) Kitchen Receptacle Requirements. Receptacles installed in a kitchen to serve the countertop surfaces shall be supplied by not fewer than two small appliance branch circuits, either or both of which shall also be permitted to supply receptacle outlets in the same kitchen and in other rooms specified in 210.52(B)(1). Additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1). No small appliance branch circuits shall serve more than one kitchen.
[ May 22, 2005, 11:02 AM: Message edited by: georgestolz ]