Hi All,
Hoping for some interpretation - 210.52 (C)(1) figure, (C)(2) and (C)(4)
Have complied with all applicable requirements as understood in 210.52(C)(2) as well as 210.52 (C)(4).
We have an island that it just over 6' in length - flat surface, with a sink that results in 11" behind the sink.
Separate work spaces which require 2 receptacles be compliant with 210.52 (C)(1) figure/picture.
On one side of the sink, there is greater than 24" inside rim of bowl to edge of counter. Inspection has cited
(C)(1), (C)(2), and (C)(4) as applicable. Hard as I've tried, I can't see the requirement for a receptacle within
24" of the sink - This is an Island, not a peninsula, not a wall space. Am I mis-interpreting the requirement
for the island receptacles?
Hoping for some interpretation - 210.52 (C)(1) figure, (C)(2) and (C)(4)
Have complied with all applicable requirements as understood in 210.52(C)(2) as well as 210.52 (C)(4).
We have an island that it just over 6' in length - flat surface, with a sink that results in 11" behind the sink.
Separate work spaces which require 2 receptacles be compliant with 210.52 (C)(1) figure/picture.
On one side of the sink, there is greater than 24" inside rim of bowl to edge of counter. Inspection has cited
(C)(1), (C)(2), and (C)(4) as applicable. Hard as I've tried, I can't see the requirement for a receptacle within
24" of the sink - This is an Island, not a peninsula, not a wall space. Am I mis-interpreting the requirement
for the island receptacles?