2-231 Log #1624 NEC-P02 Final Action: Reject
(210.52(E))
____________________________________________________________
Submitter: James Tente, City of Naperville
Recommendation: Revise text to read as follows:
For a one-family dwelling and each unit of a two-family dwelling that is at
grade level, at least one receptacle outlet accessible while standing at grade
level and not more than 2.0 m (6 1/2 ft) above grade shall be installed at the
front and back of the dwelling where the dwelling unit is located at grade level
and provided with individual exterior entrance/egress, at least one receptacle
outlet accessible. While standing from on grade level and not more than 2.0 m
(6 1/2 ft) above grade shall be installed. See 210.8(A)(3).
Substantiation: Present language is vague. The interpretation of ?accessible?
can vary greatly and is commonly misinterpreted. The panel statement for 2005
ROP 2-236 (Log #3197) clarifies the meaning of ?accessible? and should be
included in code text for clarity.
Panel Meeting Action: Reject
Panel Statement: The panel reaffirms it?s previous position that ?at grade?
means ?while standing on grade?. See the panel action and statement on
Proposal 2-230.
Number Eligible to Vote: 12
Ballot Results: Affirmative: 11 Negative: 1
Explanation of Negative:
WEBER, R.: The panel should have accepted this proposal as submitted,
when we consider the full range of the persons using the code simplified
language as recommended will solve a lot of confusion of the requirement
being encountered out in the field. The addition of the term ?while standing? at
grade will make it clear that a receptacle installed on an elevated porch, that is
accessible by stairs from grade, would not meet the requirements of section
210.52(E).