CutToTheChase
Member
- Location
- Vancouver, WA
- Occupation
- EIT
Current project is a 3-story multifamily apartment building. Units exit to a covered walkway surrounding an open-air courtyard, then through a second door down an enclosed corridor to get to the parking lot.
210.52(E)(2) requires an outdoor receptacle when "the dwelling unit is located at grade level and provided with individual exterior entrance/egress..." Does the covered walkway/open courtyard qualify as the exterior? Or is the door out to the parking lot considered the exterior entrance/egress?
Thoughts?
210.52(E)(2) requires an outdoor receptacle when "the dwelling unit is located at grade level and provided with individual exterior entrance/egress..." Does the covered walkway/open courtyard qualify as the exterior? Or is the door out to the parking lot considered the exterior entrance/egress?
Thoughts?