210.63

Status
Not open for further replies.

normbac

Senior Member
if replacing numerous discos on back of apartment buildings and there are no outlets for servicing would there be a chance of being cited for no gfi service outlets
 
I am assuming that the disconnects are for A/C units.

If you are just replacing existing disconnects then in my opinion you would not need to add a receptacle to meet 210.63. If you were adding a new A/C unit and disconnect then you would need the receptacle.

But this is definiatly a AHJ call, so my advice is to check with the AHJ.

Chris
 
if replacing numerous discos on back of apartment buildings and there are no outlets for servicing would there be a chance of being cited for no gfi service outlets

Based on the posts in this very forum I'd say there is no doubt a chance that you may be cited.

Should you be??

I say no way.
 