This spec sheet requires that if module is fed by 2- 2 wire branch circuits they are to be on the same phase. I would assume the neutral load for the module is only for led indicators & very minimal and the branch circuit neutrals are separated to respective switch legs being fed. Multiple modules can be in the enclosure
Paste link in your browser to access PDF
https://www.control4.com/docs/produ.../latest/8-channel-dimmer-data-sheet-rev-e.pdf
Required yes/no
210.7 Multiple Branch Circuits. Where two or more branch circuits supply devices or equipment on the same yoke or mounting strap, a means to simultaneously disconnect the ungrounded supply conductors shall be provided at the point at which the branch circuits originate.