Does the 2020 NEC take out the grey area on this article? Has the part about designer or owner deciding about receptacles been removed? What about the “what is a meeting room” questions. Some say their areas meeting those dimensions are “assembly areas”..
 
Meeting Rooms have been moved to 210.65

210.65 Meeting Rooms.
210.65(A) General.
Each meeting room of not more than 93 m2 (1000 ft2) in other than dwelling units shall have outlets for nonlocking-type, 125-volt, 15- or 20-ampere receptacles. The outlets shall be installed in accordance with 210.65(B). Where a room or space is provided with movable partition(s), each room size shall be determined with the partition in the position that results in the smallest size meeting room.
Informational Note No. 1: For the purposes of this section, meeting rooms are typically designed or intended for the gathering of seated occupants for such purposes as conferences, deliberations, or similar purposes, where portable electronic equipment such as computers, projectors, or similar equipment is likely to be used.
Informational Note No. 2: Examples of rooms that are not meeting rooms include auditoriums, schoolrooms, and coffee shops.
210.65(B) Receptacle Outlets Required.
The total number of receptacle outlets, including floor outlets and receptacle outlets in fixed furniture, shall not be less than as determined in (1) and (2).
210.65(B)(1) Receptacle Outlets in Fixed Walls.
The required number of receptacle outlets shall be determined in accordance with 210.52(A)(1) through (A)(4). These receptacle outlets shall be permitted to be located as determined by the installer, designer, or building owner.
210.65(B)(2) Floor Outlets.
A meeting room with any floor dimension that is 3.7 m (12 ft) or greater in any direction and that has a floor area of at least 20 m2 (215 ft2) shall have at least one floor receptacle outlet, or at least one floor outlet to serve receptacle(s), located at a distance not less than 1.8 m (6 ft) from any fixed wall for each 20 m2 (215 ft2) or major portion of floor space.
Informational Note No. 1: See 314.27(B) for floor boxes used for receptacles located in the floor.
Informational Note No. 2: See Article 518 for assembly occupancies designed for 100 or more persons.
 