In this thread Kitchen Hospital receptacles Brother brought up something I have never thought of.
Does 210.8 apply to cord connectors?
Does 210.8 apply to cord connectors?
iwire said:Brother IMO it is simply an oversight, 210.8 should be changed to say receptacles and cord connectors.
iwire said:Brother IMO it is simply an oversight, 210.8 should be changed to say receptacles and cord connectors.
augie47 said:IMHO, when you look at the definition of a "receptacle" in Art100 it covers cord connectors.
Just to stirr the pot a cord assembly would install at an outlet. Just thinkin out loud here.brother said:Please explain your interpertation,
the definition contains the phrase "A receptacle is a contact device installed at the outlet......"
So i dont see how a cord would fit this definition.
quogueelectric said:Just to stirr the pot a cord assembly would install at an outlet. Just thinkin out loud here.
augie47 said:IMHO, when you look at the definition of a "receptacle" in Art100 it covers cord connectors.
brother said:so are you putting in a proposal??It may be an oversight, but like one member stated about the Code:
"It does not say what you think it says"
"It does not say what you want it to say"
"It does not say what you feel it SHOULD say"
"It may not even say, what you heard someone said it says"
"It may not even say what the CMP really intended for it to say (because of their oversight)"
IT JUST SAYS WHAT IT SAYS.![]()
iwire said:Well is cord connector on a yoke?
'A single receptacle is a single contact device with no other contact device on the same yoke'
And if it is one and the same why are they treated separately in Article 406?
All I am saying is it says what it says and it does not say what I expected it to say.
So yes, maybe I will put in a proposal. :smile:
I believe the cord assembly being considered is one that is hardwired on the feed end and has a cord connector on the other end.quogueelectric said:Just to stirr the pot a cord assembly would install at an outlet. Just thinkin out loud here.
To me, this reads that "single receptacle" is a two word term, as is "multiple receptacle".2008 NEC Article 100 Definitions
Receptacle. A receptacle is a contact device installed at the outlet for the connection of an attachment plug. A single receptacle is a single contact device with no other contact device on the same yoke. A multiple receptacle is two or more contact devices on the same yoke.
al hildenbrand said:Therefore, 210.8 applies, because the cord cap, a contact device installed at an outlet, meets, IMO, the definition of receptacle.
The pendant cord with a cord connector is permitted elsewhere as something that is not securely fastened in place.406.4 Receptacle Mounting.
Receptacles shall be mounted in boxes or assemblies designed for the purpose, and such boxes or assemblies shall be securely fastened in place unless otherwise permitted elsewhere in this Code.
charlie b said:Help me on this one. What is a "cord connector"?
Think of the receptacle end of a standard extension cord. That female contact device is the cord connector. One can assemble the cord connector to a cord, or puchase a molded one piece cord and connector.:smile:charlie b said:Help me on this one. What is a "cord connector"?
al hildenbrand said:The pendant cord with a cord connected is permitted elsewhere as something that is not securely fastened in place.